by Joe Evans

Have you ever wondered why a motor manufacturer would state that many of their 60-Hz motors will operate on 50-Hz power as long as you reduce the nameplate voltage by 1/6?

It turns out that, unlike DC, AC voltage is a "time varying" quantity and if you alter the duration of the AC cycle, you better alter the voltage too. This is also the reason why a VFD must continuously modify its output voltage relative to its output frequency. Let's see if we can put this time varying quantity into perspective.

A good starting point is to review the wave form produced by AC. Figure 1 shows one cycle of a 460-V, 60-Hz single phase sine wave. The X-axis is time and the Y-axis is voltage intensity. It begins its cycle at 0-V, rises to some positive maximum, and returns to 0-V. It then falls to some negative maximum and again returns to 0-V. All of this occurs in just 1/60 of a second, or about 16.6 milliseconds.

pump-ed-1.jpg

The first thing we notice about this wave is that its voltage intensity varies at every single point in time. In fact, it has a value of zero at three points and is even negative during the last half of the cycle! Another observation is that the maximum voltage intensity of the upper and lower peaks is quite a bit more (about 650-V) than the 460-V we claim the curve represents. These two observations are a big part of the reason Thomas Edison almost won the war over power generation and distribution in the U.S. Although AC has several significant advantages over DC, it happens to be far more complex.

So why do we measure 460-V on a wave that varies from +650-V to negative 650-V? Could it be that 460-V is the average of all those points?

Unfortunately, it is not that simple; the average intensity would be zero since half of the wave is positive and the other half is negative. Even if we took the average of the "absolute values" it would fall well below 460-V. It turns out that it is a result of a function known as the "root mean square" (RMS), and it is the RMS voltage that you measure when you use a typical voltmeter.

To calculate RMS voltage, the intensity at every point on the curve is multiplied times itself (now the negative values become positive) and all of the results are added together. The total is then divided by the number of measurements to obtain the mean (or average) of the squares. Finally, the square root of this mean gives us the RMS voltage. It turns out that the RMS voltage will always be 0.707 times the peak voltage, and peak voltage is always 1.414 that of the RMS voltage.

Figure 2 compares that same 60-Hz wave form with one that has a frequency of 50-Hz. Both have a peak voltage of 650-V and an RMS voltage of 460-V. The major difference between the two is that the 50-Hz wave requires more time to complete one full cycle than does the one at 60-Hz (20-ms vs. 16.6-ms for the 60-Hz wave).

pump-ed-2.jpg

If you look closely at the two waves, you will also notice that the area under the 50-Hz curve appears to be quite a bit larger than that of the 60-Hz curve (focus on the positive portions of the two curves, since both have the same starting point). Since total voltage per cycle is proportional to these areas, the 50-Hz curve produces more voltage per cycle than does the 60-Hz curve. We can get a simple quantitative comparison by dividing the RMS voltage by the frequency and obtaining a quantity known as volts per hertz (V/Hz). At 60-Hz, V/Hz is 7.67 and at 50-Hz it is 9.20.

So why is this ratio important and how does it affect the operation of an electric motor?

An AC induction motor is designed to operate with a rotating magnetic field of constant strength. The magnetic field produced by the stator and the lines of flux that it generates are directly proportional to voltage and inversely proportional to frequency (flux ≈ V/Hz). If we are to keep flux (and the torque produced) constant, we must maintain a constant V/Hz ratio.

For example, a 460-V / 60-Hz two pole motor operates at a synchronous speed of one rotation per AC cycle. At 50-Hz that same motor will still operate at one rotation per cycle, but since the cycle takes longer, the stator will see a greater voltage "quantity" (volt-seconds) during that cycle. This additional voltage will generate a higher flux, which can cause magnetic saturation in the stator and result in undesirable torque characteristics and potential overheating of the motor.

So how do we cure this problem? It is pretty simple: just reduce the voltage of the lower frequency wave so that its V/Hz ratio is the same as it is for 60-Hz. Figure 3 shows the result when the 50-Hz voltage is reduced. At a reduced RMS voltage of 380-V (5/6 of 460-V), the area beneath the 50-Hz curve now appears equal to that of the 60-Hz curve. This is confirmed by the equal values (7.67) of the two V/Hz ratios.

pump-ed-3.jpg

When frequency and the resulting motor speed are changed, the applied voltage is always changed in the same proportion. This allows magnetic flux and the torque it produces to remain constant regardless of speed.  In the case of a 60-Hz motor running on 50-Hz power, voltage is reduced by 1/6. In the case of VFD control, the voltage is varied in proportion with every single change in frequency, whether up or down.

There are, however, VFD applications (centrifugal pumps, for example) where constant torque is not a requirement. In such cases, voltage can be reduced below the normal constant V/Hz level at lower speeds. We will address this control technique and its effect on power and efficiency in a later column.